    The low-pressure switch setting principle

    Time: 2025-07-29 02:07:31 Click:0

    Here is the professional English translation of the low-pressure switch setting principles:


    ? I. Core Operating Principle


    Low-pressure switches operate through ?hydraulic-mechanical-electrical conversion?:


    Pressure Sensing?:

    Pipe network fluid pressure acts on internal diaphragm/piston

    Springs drive mechanical displacement to trigger switch when pressure drops

    Signal Conversion?:

    Displacement activates micro switch, converting motion to electrical signal

    Normally Open (NO) contact closes to complete circuit, initiating pump start signal

    Dual Output?:

    Two independent contacts: One interlocks pump start, the other feeds back to fire control panel


    (Insert schematic: Micro switch & diaphragm internal structure)


    ?? II. Electrical Control Logic

    Terminal Type? ?Function? ?Connection Target?

    Common (COM)? Reference potential 24V power input

    NO (Normally Open)? Closes when pressure low Pump control cabinet start terminal

    NC (Normally Closed)? Closes normally (optional) System status monitoring


    Pump Interlock Logic?: Pressure below setpoint → NO-COM conducts → Directly triggers pump start (independent of fire panel)


    ?? III. Threshold Setting Mechanisms

    Mechanical Adjustment?

    Knob Calibration?:

    Adjust spring preload: Clockwise ↗? increases pressure, counterclockwise ↘? decreases

    Secured by hex bolts to prevent vibration loosening

    Differential Control?:

    Start value (e.g., 0.05MPa) and stop value (e.g., 0.15MPa) must maintain ≥0.05MPa difference

    Electronic Configuration?

    Long-press setting key to enter programming mode

    Use ▲/▼ keys to adjust start pressure (e.g., ?0.03MPa?) and stop pressure (e.g., ?0.12MPa?)

    Save and switch to operational mode to activate settings


    (Insert comparison card: Different switch operation interfaces)


    ?? IV. Critical Installation Standards

    Location Requirements?:

    Must be installed on ?main discharge pipe? of fire pump to directly sense network pressure

    Range Selection?:

    Range ≥1.6MPa and ≥2× design pressure

    Wiring Protection?:

    Pump interlock wires require ?24V relay? isolation from high voltage

    Metal housings must be grounded for EMI protection

    ?? V. Workflow Example (Fire Protection System)

    mermaid

    Copy Code

    graph LR

    A[Pipe pressure drops] --> B[Diaphragm actuates micro switch]  

    B --> C{NO contact closes}  

    C --> D[Direct pump start]  

    C --> E[Signal to fire control panel]  



    (Workflow basis: Fire protection standards)


    Post-commissioning?: Simulate 3 pressure cycles to verify actuation consistency


    (Technical diagrams and multimedia placeholders retained)